I don't have plc connected to opc server still I want real time data from plc in any format.I want timer's ACC data which I have to process on it further. How can I? please give steps of it coz im new user of plc. I have micrologix 1400 plc of allen Bradley.

share|improve this question

1 Answer 1

You can use RSlinx to setup a "Topic" that allows Excel to to communicate with the PLC via DDE. Take a look at this example: http://forums.mrplc.com/index.php?autocom=downloads&showfile=820

or Google: RSlinx DDE Excel, then you will find a lot of help.