2

I am not 100% sure if this fits StackOverflow or I should have posted on a more automation-specific StackExchange site, so my apologies to the moderators anyway.

I am trying to program an ABB PM564 PLC with CodeSys, which controls a motor connected to its ouputs (FORWARD is output0, REVERSE is output1). The scenario inputs are a POWER button (input0) which turns on/off the motor and a SENSOR (input1) which would cause the motor to invert its rotation when activated.

Cause the instant reverse would cause a jam to the motor I have to use a delay function (Timer On-Delay, aka TON) to pause the motor for an internal of 1sec, before changing the rotation.

Here is the block of code in Structured Text language:

FUNCTION_BLOCK SWITCH
VAR_INPUT
    POWER : BOOL;
    SENSOR : BOOL;
END_VAR
VAR_OUTPUT
    FORWARD : BOOL;
    REVERSE : BOOL;
END_VAR
VAR
    switch: BOOL;
    delay : TON;
END_VAR

-

delay(IN:=switch, PT:=T#1000ms);

IF POWER THEN
    IF NOT(FORWARD OR REVERSE) THEN
        FORWARD:=TRUE;
        REVERSE:=FALSE;
    END_IF;
ELSE
    FORWARD:=FALSE;
    REVERSE:=FALSE;
END_IF;

IF SENSOR THEN
    switch:=TRUE;
END_IF;

IF switch THEN
    IF FORWARD THEN
        FORWARD:=FALSE;
        IF delay.Q THEN
            REVERSE:=TRUE;
            switch:=FALSE;
        END_IF;
    END_IF;
    IF REVERSE THEN
        REVERSE:=FALSE;
        IF delay.Q THEN
            FORWARD:=TRUE;
            switch:=FALSE;
        END_IF;
    END_IF;
END_IF;

The problem is that IF block statement at line 25 of the implementation code does not seem to execute, causing the motor to pause for a sec and continue to rotate FORWARD every time..

  • Isn't there any timer reset? Also have you tried to reverse the fwd and rev commands and see if the logic reverses? – Abhishek Bansal Nov 25 '13 at 12:51
  • For how much time is the sensor on? – Abhishek Bansal Nov 25 '13 at 12:52
  • It seems it only executes the first IF block inside IF switch THEN. If I put the IF REVERSE THEN first it switch to REVERSE but it continues after every pause to rotating on REVERSE... The SENSOR should be turned off instantly as it is a button, so I pass its value to switch var to avoid the timer function to reset instantly. – lephleg Nov 25 '13 at 12:59
2

It's my guess but the problem maybe here:

IF POWER THEN
    IF NOT(FORWARD OR REVERSE) THEN
        FORWARD:=TRUE;
        REVERSE:=FALSE;
    END_IF;

This code shall be executed on every scan of the PLC. So when the timer is running, then neither of FORWARD or REVERSE is TRUE. Hence this if statement executes and makes FORWARD = TRUE.

Try this:

delay(IN:=switch, PT:=T#1000ms);

IF POWER THEN
    IF (NOT(FORWARD OR REVERSE) AND NOT(switch)) THEN
        FORWARD:=TRUE;
        REVERSE:=FALSE;
        REV_DELAY:=FALSE;
        FWD_DELAY:=FALSE;
    END_IF;
ELSE
    FORWARD:=FALSE;
    REVERSE:=FALSE;
END_IF;

IF SENSOR THEN
    switch:=TRUE;
END_IF;

IF switch THEN
    IF FORWARD THEN
        FORWARD:=FALSE;
        REV_DELAY:=TRUE;
        FWD_DELAY:=FALSE;
    END_IF;
    IF REVERSE THEN
        REVERSE:=FALSE;
        FWD_DELAY:=TRUE;
        REV_DELAY:=FALSE;
    END_IF;
END_IF;

IF (switch AND delay.Q) THEN
  REVERSE:=REV_DELAY;
  FORWARD:=FWD_DELAY;
  REV_DELAY:=FALSE;
  FWD_DELAY:=FALSE;
  switch:=FALSE;
END_IF;
  • hmmm maybe you have point, but in that case I think it wouldn't pause at all. It would change instantly after I put FORWARD:=FALSE; – lephleg Nov 25 '13 at 13:23
  • @LePhleg It will keep toggling itself till the timer is running because the timer loop will continue making it false again. In any case, try to correct it and see. – Abhishek Bansal Nov 25 '13 at 13:25
  • so whats your suggestion to change it to? – lephleg Nov 25 '13 at 13:36
  • Simply add a check here IF NOT((FORWARD OR REVERSE) AND !switch). If switch is false, only then the statement shall execute. – Abhishek Bansal Nov 25 '13 at 13:40
  • 1
    @LePhleg I have updated my answer. – Abhishek Bansal Nov 25 '13 at 13:56
0

Watch delay.Q, because it seams never to be true.